That Man
- California, United States
- Electrical Designer
Mike Holt friends,
I have a design problem I want your opinion on, which may have an established solution, since I imagine this problem is often faced for city utility installations. I'm designing a relatively large underground conduit system (industrial, not for a utility). To make the system easy to use, I am placing 4'W x 4'L x 4'D concrete pull boxes at strategic locations, to allow for easy cable pulling, while also making the system easy to expand at a later date, if necessary. It occurs to me that there may be a problem, however. I'm running both power and instrument cables in my conduit system. I separate the analog from the power by using different conduits, but within the pull box itself, there is no separation. I don't think insulation will be an issue, since it's easy to simply spec 600V insulation for power as well as control cables. The two elements of my problem are:
1. Is there any code violation using a pull box as I describe for multiple service types (DC analog, 120VAC, 480VAC all together)? I couldn't find any, but I also couldn't find any specific allowances for this scenario either.
2. I'm worried about signal interference between the power and instrument cables when they run through these boxes without a barrier between them. Does anybody have any experience with this?
Thank you all in advance for your help.