mstrlucky74

Senior Member
Location
NJ
What type of cable(power limited or non-power limited are used for the following ckts. I know you can use thhn in some instances but disregarding that for now.

IDC/SLC ckts.
NAC ckts
24v power for fire alarm.

thanks
 

GrayHair

Senior Member
Location
Nashville, TN
In my experience, cable/wire type (power limited or non-power limited) was always determined by the power supply (FACP, NAC Booster, Aux Power Supply, etc) for the circuit. I haven't kept up with codes since retiring.
 

luckylerado

Senior Member
What type of cable(power limited or non-power limited are used for the following ckts. I know you can use thhn in some instances but disregarding that for now.

IDC/SLC ckts.
NAC ckts
24v power for fire alarm.

thanks


FPLR or FPLP (riser or plenum) are very common for fire alarm systems.
16 or 18-2 non-shielded for SLC/IDC
14-2 non-shielded for horn and strobe NACs and 24V.
16-2 Shielded for voice or audio speaker appliance

Those are typical. Voltage drop should be considered when sizing. Follow manufacturer instructions. Some SLC/IDC are shielded.

Other factors that should be considered:

?pipe or free air
?Length
?Classification of space
?Sharing an enclosure with 120V power
?Temperature and environmental conditions
?survivability requirements or project
 
What kind of cable?

What kind of cable?

Right, what he said above. I don't think you'll ever use non-power limited, I never have. I think that was what they used back in the day.

John
 
Last edited by a moderator:

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Right, what he said above. I don't think you'll ever use non-power limited, I never have. I think that was what they used back in the day.

John
lowvoltageeng.com

Early Pyrotronics ionization smokes operated at 250vdc.
 