Hoowdy folks
I am reworking a job where the original electrician bailed on my customer. We are through most of their mischief but have one very large potato still cooking away. The owners thinking they would save some $$$ bought a used HVAC unit (not roof top out back pad mount) however not knowing they bought a 460V (480) unit and this building only has 208/120V wye. A new 10 ton unit would cost them 6K. I can get a transformer used (75KVA) for around 1,000 ish looking on e-bay. I have no clue on how to calculate for the locked rotor current (startup) VS xfmr size a 45KVA would do so per min circ size shown but as hunch being able to get a 75KVA for the same price as a 45 makes me guess a 75 would handle to start up better. HOWEVER I hear there is a difference between step up and step down transformers, all the ones I see are 480 prim to 208/120 sec so I would have to wire this backwards. I can not see using a neutral would be needed on the 208V (now) prim side (wye would it be, bad pun) but the bigger question is this a code violation, a breaking of natural law and if so wye on either? The power company wants way more to put in 480 and counting the switch gear etc a right voltage unit wins over that possibility. My real gut feeling is for them to get the right voltage brand new warrantied unit for 6K but hey will at least try to figure out the option here.
I am deliberately making your mistakes for you, just to help you learn faster, yup I got those big of shoulders...