I have a situation wherein a 50KVA, 240/120volt, single phase, 3-wire step down transformer is fed from a 480volt meter/service disconnect.
The secondary of this transformer feeds an automatic transfer switch (ATS), which in turn feeds a panelboard with 200amp MCB. The step down transformer, ATS and panelboard are all in the same line up and within sight of each other. Distances are the following: From service disconnect to ATS = 8feet; from ATS to panelboard = 5feet. One jurisdiction did not require overcurrent protection on the secondary side of the transformer ahead of the ATS; another jurisdiction is requiring an OCP ahead of the ATS in compliance with NEC 240.21 requirements. What is the correct interpretation of NEC 240.21 (C) on the foregoing situation? Thanks.
The secondary of this transformer feeds an automatic transfer switch (ATS), which in turn feeds a panelboard with 200amp MCB. The step down transformer, ATS and panelboard are all in the same line up and within sight of each other. Distances are the following: From service disconnect to ATS = 8feet; from ATS to panelboard = 5feet. One jurisdiction did not require overcurrent protection on the secondary side of the transformer ahead of the ATS; another jurisdiction is requiring an OCP ahead of the ATS in compliance with NEC 240.21 requirements. What is the correct interpretation of NEC 240.21 (C) on the foregoing situation? Thanks.