m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Jan 17, 2016 #1 Hi everyone, Which we considering for OCPD KAIC Calculation the asymmetric ka or symmetric ka , from my first calculation it seems the smaller i.e. symmetric. Am i right?
Hi everyone, Which we considering for OCPD KAIC Calculation the asymmetric ka or symmetric ka , from my first calculation it seems the smaller i.e. symmetric. Am i right?
m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Jan 17, 2016 #2 Any feedback
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Jan 17, 2016 #3 Symmetrical.
m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Jan 17, 2016 #4 Thanks
H Haji Banned Location India Jan 18, 2016 #5 But symmetric calculation takes into account asymmetric DC by a suitable factor. Isn't it?
B Bugman1400 Senior Member Location Charlotte, NC Jan 18, 2016 #6 I guess it depends on your application. For Medium Voltage (MV) and higher, I say you should consider subtransient (asymmetric).
I guess it depends on your application. For Medium Voltage (MV) and higher, I say you should consider subtransient (asymmetric).