AHarb
- Atlanta, GA
Hi,
We had something occur yesterday that I couldn't figure out. We were tying two distribution circuits together and had an issue when "phasing" the normal open point. We use phasing sticks that measure the voltage from one open point to another to verify that the phases being tied are identical. In this scenario, we were tying the circuits together through a large (5000 kVA) transformer. The measured voltages across the open points for phases A and B were 0 V indicating that there were no phase shifts and they could be tied. The measurement taken across the phase C open points showed 4 kV. The line/ground measurements were 15 kV at all 6 points so it seems like there was a small phase shift at the phase C normal open point. We think this was due to the large 5000 kVA (14.4 kV/7.2 kV wye/wye) transformer. Can we calculate the phase shift with the given information? It seems like it should be possible, but I can't remember how to do it.
Thanks in advance.
Adam
Thanks in advance.
Adam