(a) Common Grounding Electrode Conductor. The
common grounding electrode conductor shall be permitted
to be one of the following:
(1) A conductor of the wire type not smaller than 3/0 AWG
copper or 250 kcmil aluminum
(2) The metal frame of the building or structure that complies
with 250.52(A)(2) or is connected to the grounding
electrode system by a conductor that shall not be
smaller than 3/0 AWG copper or 250 kcmil aluminum
(b) Tap Conductor Size. Each tap conductor shall be
sized in accordance with 250.66 based on the derived ungrounded
conductors of the separately derived system it
serves.
Exception: If a separately derived system originates in
listed equipment suitable as service equipment, the grounding
electrode conductor from the service or feeder equipment
to the grounding electrode shall be permitted as the
grounding electrode conductor for the separately derived
system, provided the grounding electrode conductor is of
suffıcient size for the separately derived system. If the
equipment ground bus internal to the equipment is not
smaller than the required grounding electrode conductor
for the separately derived system, the grounding electrode
connection for the separately derived system shall be permitted
to be made to the bus.