Micro-managing
Micro-managing
Please don't worry about micro-managing because I am learning and everything so far has been great and I thank everyone for making me smarter. My Chief Petty Officer used to tell me to go get a hammer. For a while I would say, Why do you need a hammer Chief? and he would say, Because it is smarter that you are. :lol: Eventually he stopped but then he switched to 'a box of rocks' reference.
Finally, he started treating me like an equal - once I made Chief.
Anyway, I think I am on track now except for one point. The disconnect has a slide switch which I presume could be a form of fuse but I would like to clarify that in my hammer like brain.
I know what the "normal" fuses look like and a "normal looking" circuit breaker looks like. This disconnect doesn't match either of those "normal" looking devices. This one is a sliding switch. I have it in my hand now. It says: "This switch is suitable for use on a circuit capable of delivering not more than 10,000 amperes, RMS symmetrical, 240 volts maximum when protected by --> 60 ampere maximum fuses, or circuit breaker rated 60 amperes bla bla bla.
Please tell me where my thinking gets off track. Since this "switch" says 'when protected by' 60 amp fuse or breaker And the circuit breaker they left with me is a 60 amp breaker And the whip they left with me is #8 hots and THHN 10 gage gnd.
So so with all of that, me thinks they think that the whole 60amp circuit is OK meaning that they hadn't read the spec plate on the compressor unit which says 'max fuse amps or max circuit breaker 40'. Thus they are wrong and I
should not let them proceed with that plan?