Used to believe otherwise, but now I don't believe there is such a thing as a consumer-owned service transformer. Code permits certain items to be connected to service conductors before the service disconnecting means. A transformer is not one of them.
On the utility side of the service disconnecting means (of a grounded system), the grounded conductor is use to bond all conductive enclosures and raceways. 250.30(A)(1) Exception No. 2 does not apply.
250.30(A)(1) Exception No. 2 permits an outside SDS transformer supplying a building or structure to be connected in a manner quite similar to a service transformer. To do so, there can be no SSBJ as permitted by 250.30(A)(2) Exception. This latter exception was finally realized and put in the 2014 Code... but in prior editions, it is impossible to bond at both the transformer and its disconnecting means without creating a parallel path for grounded conductor current.