Hello Everyone,
I just joined this forum yesterday and would like to ask for your help and support...
I encountered something that maybe some of you already had this experience about UPS [3PH, 440V/200-100V, 500KVA]. After it was energized and on-line for 2 months, the unit experienced a critical alarm due to DC Over Voltage. It transferred to Bypass when the alarm happened. When it was reset, the UPS went back to normal. The findings of UPS vendor is due to the CPU board. It was replaced with a new one to further investigate what really happened to the CPU board. It was retested at the UPS factory and simulated various tests (i.e. visual check, noise test, control power voltage test, etc.). After all tests, the UPS vendor concluded that the main root cause of alarm is the CPU board internal memory. I am worried that this may happen again in the future.
I am just hoping someone experienced the above and any comments/suggestions would be much appreciated.
Thanks
Vestre
Thanks
Vestre