Dedicated Space
infinity
New Jersey
Journeyman Electrician
110.26(F) is for locked rooms are these panelboards within the locked rooms? Even if they are I see no relief from the standard dedicated space rules.
charlie b
Lockport, IL
Retired Electrical Engineer
Steve, I think you have a typo. Did you mean to refer to 110.26(E)? If so, then I agree with Rob that your answer is "yes, the dedicated space rules do apply."
Greg1707
Alexandria, VA
Business owner Electrical contractor
panels on wall of kitchen counter space
I have often wondered about this. I have been in many high rise/apartments where the panel is on the wall of the kitchen counter. I always have to lay on the counter top in order to open up the panel. These are building from the 1970's.
Has anything changed over the years with the working space requirements?
On the other hand, maybe the kitchens have been renovated over the years and cabinets have been placed in front of the panels?