- Massachusetts
RE: smokes being on a dedicated circuit. I'm pretty sure that is prohibited by the NFPA 72. It requires the smokes to be on a general lighting circuit.
Does NFPA 72 even apply to residential smoke alarms?
We actually don't install AFCIs on lighting circuits, so that's where we pull off of.
I'm confused. What code cycle are you on?
I don't understand2008, been on it since 2010
I don't understand
The 2008 code requires AFCI protection for branch circuits that supply outlets in most of the rooms in the house. Light fixtures are installed at outlets and the lighting branch circuits require AFCI protection under the 2008 NEC.
I actually try not to dedicated the smokes on purpose. My thought is that if some stupid HO pulls all of the batteries and the circuit trips for some reason, they could feasibly never know if they're off, so I always put them on with something else, nonAFCI protected of course.
You're absolutely right, the light box locations are considered outlets and the lights themselves, utilization equipment. Let's just say my company has been in the area 50+ years and the owner is personal friends with just about every inspector in the area. Benefits of those friendships I suppose. If I viewed it as substandard work, I'd probably make some noise about it, just as the inspectors would call us on it if they did as well. But after talking to a couple of them about it, they both seemed like they'd rather have smokes on a lighting circuit that wasn't AFCI protected.
Still has been wrong from nearly day one of AFCI requirements existing in the NEC.
Inspectors should not be allowing certain circumstances that are violations just because they are friends with a particular contractor or owner. Though it does happen sometimes it is not right.
I don't and can't dispute that it's not compliant, but clearly you didn't read my post thoroughly. The inspector didn't not call it as a favor, he preferred that the smokes be on a lighting circuit that was not AFCI protected.Still has been wrong from nearly day one of AFCI requirements existing in the NEC.
I can understand maybe wanting the smoke alarms on a non AFCI circuit - but the more recent the NEC edition used the more the number of lighting outlets there are that require AFCI protection as well.I don't and can't dispute that it's not compliant, but clearly you didn't read my post thoroughly. The inspector didn't not call it as a favor, he preferred that the smokes be on a lighting circuit that was not AFCI protected.
Sent from my SCH-I545 using Tapatalk