Although when sizing the breaker panels and the service you should run through the 120% rule totally separate from the load calcs, just in case there is a squeeze there.
Calculations are for loads and the solar does not add loads but takes some load off the service. The problem is you cannot deduct that extra support from the solar panels because it is not always able to reduce the load on the service. For example long periods of rainy weather- no sun.
For any panels or feeders which carry backfed power from the PV inverter(s) the sum of the backfeed amps and the normal feed breaker amps must not exceed 120% of the feeder or bus bar rated ampacity.I got the "PV is not load" part.
I do not understand the "120% rule and squeeze" part.
Thanks
It is 120% of the bus rating.
Some 200A panels have a 225A bus, potentially giving you a 7.0A allowance.
(45A + 25A)
(45A + 25A)
What is the NEC section on the rule? I found it in the James Dunlap book but can't find it in the NEC.
Thanks
It doesn't. It is not a load. And you cannot count on it to offset loads either.
In particular there will be situations such as solar farms where the generated lower is far higher than any local loads. In such cases circuit sizing will depend, as set out in the NEC, by the generation rather than the loads. But even in those cases the generation will not add to the loads in reaching that result.On site power production is not a load it is a source. However supply conductors and equipment need to factor in any impact it may have on the current those items carry or potentially could carry.
The grid becomes the load.... if you have more production then load - you better at least have supply equipment that can handle the production ability.
But your on site load offsets this, is there anything in art 220 that tells us how to calculate for on site production that backfeeds the grid? I could be wrong but I don't think so. Art 220 is primarily for on site loads. Those on site production loads are covered in 690, 694, or whatever article applies to the type of production.