- NE Nebraska
Not one that would require a handle tye.
JAP>
Correct on that.
JAP>
I had an inspector leave me a message and said I couldn't use two single pole 20 amp breakers with a handle tie Can someone point me in the right direction of this code? Would this also apply to a wall heater circuit?
The inspector is wrong. As others have pointed out, 240.15(B)(2) allows this assuming this is a 120/240 system and the breaker has a 120/240 rating. AFAIK as a practical matter all 1 pole breakers today have a 120/240 rating.
I agree, the inspector is incorrect given the nature of the load and no MWBC present.
The single pole breakers I am using are rated 120/240 volt. It says it right on the side of the breaker. The circuit he was referring to was my 12/2 nm-b that I have going to a 60 amp non fused disconnect that is for a ductless mini split heat pump.
what does "identified handle tie" refer to in 240.15 (b) (2)
this is the handle tie I'm using
http://www.acdcusa.com/ths1-cutler-...bd-breakers/?gclid=CJr9_vzn2soCFVFlfgod1DsBQA
Identified (as applied to equipment). Recognizable as suitable for the specific purpose, function, use, environment, application, and so forth, where described in a particular Code requirement.
Informational Note: Some examples of ways to determine suitability of equipment for a specific purpose, environment, or application include investigations by a qualified testing laboratory (listing and labeling), an inspection agency, or other organizations concerned with product evaluation.
Here is the Article 100 definition:
Does the inspector have an issue with the handle tie that was used or the two single pole CB's in lieu of a 2 pole?