Hi All. I've learned much from the forum discussions, but I would like some feedback on code regarding the 120% rule (705.12(D)(2)) and minimum service amperage to a residential home (230.79(c))
We are proposing to install a 30A backfed breaker on a 100A rated service panel with 100A rated bussing. We thought that a workaround to the 120% rule would be to derate the main service breaker from 100A to a 90A breaker. However, we are getting denied from the AHJ citing the aforementioned code that a minimum of 100A service needs to be available to a residential home.
My questions
1) Does the 100A minimum service NEC code only apply to a new construction?
2) Can an existing service be modified such as our de-rating of the main breaker to 90A?
Thanks in advance for any feedback
My questions