Sizing EGC for Voltage Drop

Status
Not open for further replies.

mjc1060

Senior Member
I have a 120V 20A circuit that is 500 ft long. If the circuit (hot and neutral) conductors are increased to #8 AWG what size EGC does the NEC require?
Where can I find the NEC reference that covers this?:?
 

kwired

Electron manager
Location
NE Nebraska
The fact the EGC needs increased proportionally to the increase of the ungrounded conductors makes this easy to figure out with 15, 20 and 30 amp circuits as the EGC for those is same size as minimum size ungrounded conductor (as a general rule anyway).

Where it gets more complicated is with larger then 30 amp circuits where the EGC isn't typically required to be same size as the ungrounded conductors.
 

Carultch

Senior Member
Location
Massachusetts
The fact the EGC needs increased proportionally to the increase of the ungrounded conductors makes this easy to figure out with 15, 20 and 30 amp circuits as the EGC for those is same size as minimum size ungrounded conductor (as a general rule anyway).

Where it gets more complicated is with larger then 30 amp circuits where the EGC isn't typically required to be same size as the ungrounded conductors.


Here's a simple example.

Consider a simple 40A circuit.

Default wire size is #8 Cu
Default ground size is #10 Cu

Suppose we need to upsize the ungrounded conductors to #6 Cu for voltage drop reasons. The ratio of cross sectional areas is 26.3 kcmil / 16.5 kcmil = 1.59. This ratio must also be the kcmil ratio of the EGC. #10 is approximately 10 kcmil. Multiply by 1.59 and you get 15.9 kcmil. The next standard wire size is #8 Cu, which has 16.5 kcmil of cross sectional area.

Conclusion:
#6 Cu wires with #8 Cu ground.

In general, if you increase the wire size by X number of sizes, you'll usually increase the ground size by X number of sizes.
 

kwired

Electron manager
Location
NE Nebraska
Here's a simple example.

Consider a simple 40A circuit.

Default wire size is #8 Cu
Default ground size is #10 Cu

Suppose we need to upsize the ungrounded conductors to #6 Cu for voltage drop reasons. The ratio of cross sectional areas is 26.3 kcmil / 16.5 kcmil = 1.59. This ratio must also be the kcmil ratio of the EGC. #10 is approximately 10 kcmil. Multiply by 1.59 and you get 15.9 kcmil. The next standard wire size is #8 Cu, which has 16.5 kcmil of cross sectional area.

Conclusion:
#6 Cu wires with #8 Cu ground.

In general, if you increase the wire size by X number of sizes, you'll usually increase the ground size by X number of sizes.
Now stir pot a little.

Take a 60 amp circuit -

default wire size 6 AWG
default EGC 10 AWG



Why is 10 AWG sufficient to protect circuit with 6 AWG conductor and 60 amp OCPD, yet if we leave everything else the same but change the OCPD to a 40 it is now too small?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Now stir pot a little.

Take a 60 amp circuit -

default wire size 6 AWG
default EGC 10 AWG



Why is 10 AWG sufficient to protect circuit with 6 AWG conductor and 60 amp OCPD, yet if we leave everything else the same but change the OCPD to a 40 it is now too small?
Because CMP 5 refuses to accept proposals that would tie the required size of the EGC to the size of the ungrounded conductors and not to the size of the OCPD. Such a change in 250.122 would eliminate this issue.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Now stir pot a little.

Take a 60 amp circuit -

default wire size 6 AWG
default EGC 10 AWG



Why is 10 AWG sufficient to protect circuit with 6 AWG conductor and 60 amp OCPD, yet if we leave everything else the same but change the OCPD to a 40 it is now too small?

:?

So, with same sized ungrounded conductor (6ga here), downsizing from 60A breaker to 40 requires EGC be upsized from #10 to, what, #6? What's the code section, and why does it have to be done?
 

Carultch

Senior Member
Location
Massachusetts
:?

So, with same sized ungrounded conductor (6ga here), downsizing from 60A breaker to 40 requires EGC be upsized from #10 to, what, #6? What's the code section, and why does it have to be done?

We're talking about an unintended loophole to this code rule, where the consequences of the rule as written can yield counterintuitive results. And there simply is no explanation for it, other than that is the way the NEC is written.

The underlying reason why this requirement exists, is that upsizing the conductors usually means that you've upsized them to curtail voltage drop due to significant length. And if the length is significant for the wires, it is also significant for the OCPD in its ability to provide an effective ground fault current path. So to improve the EGC's ability to fulfill its purpose when length is significant, it gets increased in size to improve the EGC conductance. What if the ungrounded conductors were increased in size for other reasons than voltage drop (using up leftover wire, terminal minimums that are larger than the NEC required size, etc)? Well, for the simplicity of the inspectors, the NEC says that it doesn't matter the reason.

Perhaps a way to make the rule to eliminate this blindspot, is if the ungrounded size exceeds the minimum size that has sufficient ampacity for the default EGC's maximum corresponding OCPD, then the EGC needs to be upsized proportionally for the ratio of the ungrounded conductor cross sectional area to that which would have sufficient ampacity for the EGC's maximum corresponding OCPD. I can't think of a way to clean up this language for a better understanding, so perhaps it needs an example.


***** Caution: this is not an NEC compliant example - it is a hypothetical example only **************
Given: a 40A circuit, which requires upsizing wires to #4 to curtail voltage drop.

Default wire=#8Cu
Default ground = #10 Cu

Maximum OCPD for a #10 Cu ground = 60A
Corresponding wire to a 60A OCPD = #6 Cu

Wire is upsized above what it could be for a 60A breaker (corresponding to the maximum breaker for #10 EGC) by a ratio of #4 to #6, which is a ratio of 41.7/26.3 = 1.59. Therefore, the EGC is upsized from #10 to #8.

This algorithm is very confusing, much more than the current rule. What it essentially does, is puts the OCPD standard sizes into "bins" based on the 250.122 table. And if you upsize above the minimum size for the largest breaker in the actual breaker's "bin", then you correspondingly upsize the ground.
 
Last edited:

Carultch

Senior Member
Location
Massachusetts
Now stir pot a little.

Take a 60 amp circuit -

default wire size 6 AWG
default EGC 10 AWG

Why is 10 AWG sufficient to protect circuit with 6 AWG conductor and 60 amp OCPD, yet if we leave everything else the same but change the OCPD to a 40 it is now too small?


Here's another example to stir the pot. Consider parallel sets of conductors for very large circuits.

Given a 400A circuit, that requires a total of 800 kcmil to curtail voltage drop, yet the equipment terminals are limited to 750 kcmil. Also, good luck finding any 800 kcmil copper.

The default EGC is #3 Cu

For the ungrounded conductors, we have three options:
A: The default size for a single wire per phase is 600 kcmil Cu.
B: The default size for two wires per phase in the same conduit is #4/0 Cu
C: The default size for two wires per phase in separate conduits is #3/0 Cu

To achieve 800 kcmil, the solution is to use 2 parallel sets 400 kcmil.

So what then becomes our upsize ratio, that must be used for upsizing the EGC?

A: (400 + 400)/600 = 1.33333
B: (400 + 400)/(212 + 212) = 1.887
C: (400 + 400)/(168 + 168) = 2.38

A still meets the intent of the code rule, but the NEC wording doesn't clearly indicate that this is an acceptable way to do it. Certainly it would be the most economical solution, if allowed.
B would only make sense, if the intended installation has conductors routed in a shared conduit, just like the starting point for the calculation.
C would be the conservative solution, if the parallel sets are run in separate conduits
 

tom baker

First Chief Moderator
Staff member
Because CMP 5 refuses to accept proposals that would tie the required size of the EGC to the size of the ungrounded conductors and not to the size of the OCPD. Such a change in 250.122 would eliminate this issue.

Right, that's the way the physics of this would work, larger wire, more fault current.
I heard of an example for a 120V circuit that went 1/4 mile with 250 AL for a traffic signal flasher..
 

rlundsrud

Senior Member
Location
chicago, il, USA
I am confused, if you are running a distance of 500 feet, wouldn't you need at least #2 conductors? I can't imagine that #8 could handle that distance and maintain<3% vd. You might want to check your numbers.
 

jumper

Senior Member
I am confused, if you are running a distance of 500 feet, wouldn't you need at least #2 conductors? I can't imagine that #8 could handle that distance and maintain<3% vd. You might want to check your numbers.

OP never said VD had to be limited to <3%.

OP's load may be able to handle a greater VD.

Remember that except for a few cases, VD is not a NEC requirement.
 

Carultch

Senior Member
Location
Massachusetts
Right, that's the way the physics of this would work, larger wire, more fault current.
I heard of an example for a 120V circuit that went 1/4 mile with 250 AL for a traffic signal flasher..


A larger wire doesn't necessarily cause more fault current. A larger wire just impedes the fault current less than what a smaller wire at the same length would do.
 

kwired

Electron manager
Location
NE Nebraska
A larger wire doesn't necessarily cause more fault current. A larger wire just impedes the fault current less than what a smaller wire at the same length would do.
Which will allow more fault current to flow;)

Source impedance may complicate this in some cases though.
 

Carultch

Senior Member
Location
Massachusetts
Tom's point was simply that given the same source a larger wire results in more fault current.

I agree with him.


True.

However, consider the entire reason the conductor is larger than it needs to be (for ampacity alone) in the first place. Considering identical sources, which do you think has greater fault current at the load end? A small conductor on a short length circuit? Or a large conductor on a long length circuit? Suppose they are both selected to have the same percentage voltage drop, and therefore would have the same total conductor resistance. Would you expect fault current to be less, greater, or equal on the larger/longer circuit?
 