you'll never pass if you keep thinking like that
he gave us the total reactance Xc
by you calculations a 7kva will do
but charging kva is 17kva
that xfmr won't last too long
using your numbers charging kva is 50
you 7 kva will last even less
keep trying
he asked the ngr current value, not the xfmr kva
We don't spoon-feed people here, we assume posters are big enough to do some calcs of their own, that's why!:lol:
Given the grounding transformer kVA, you can compute for the resistor values (power rating and resistor current). The resistor power rating will be matched with the transformer kVA.
BTW, you won't pass your subject if you're lazy and don't do honest research.
Here's an additional literature re grounding transformer primary voltage rating. LINK
Proceed to p. 12 for the "primary voltage rating" of the grounding transformer. Come back here and say again how "silly" old people are, will ya?:rant:
As to the "overload factor" (10.5 for 10-second rating) on transformers used in grounding, please spend some more time researching. Tip: it's an IEEE document.
Remember, engineers stand on the shoulders of the giants of their trade!