travislsuttle
- US
What are the clearances for a disconnect for a condensing unit outdoor
Sent from my SM-G920T using Tapatalk
I thought since a breaker controlled the disconnect 110.26 didn't apply
AHJ is saying 30 inches I was hoping I could find some help as I don't have 30 inches on most of these units
To do a hot-dead-hot check on the feed to the A/C?Why would you work on an energized disconnect when there is a breaker controlling it. The disconnect is just a means to make the condensing unit you plan to work on not energized.
The load side of the local disconnect, fused or not, would be the very first place where many service techs would check for power if there was a service call. Based on that, many AHJs required 110.26 work spaces for a disconnect at a AC unit.