steve holt
Member
- Location
- Hawaii
How do I size my fire pump feeders. I have a 1400A Service SWBD that I am tapping off of, feeding a 1000A stand alone breaker enclosure. From the 1000A breaker I am feeding the normal side of the fire pump ATS/controller. The fire pump is 125HP and has a locked rotor rating of 909A and FLA rating of 142A. The feeder from the 1000A to the FP controller is currently 500MCM copper (I believe this is oversized unless 695(C) doesn't apply), and the feeder from the service SWBD to the 1000A is two sets of 900MCM copper. My question is, does the feeder tap from the 1400A to the 1000A need to match the 1000A overcurrent device rating, or can it be sized based on 695.6(C)1.? What about the feeder from the 1000A to the FP controller?