250.52(A)(1) says metal underground water pipe is a grounding electrode. Would that also include the UG supply for fire sprinkler piping? I don't see anything that would exclude it.
It looks to me like 250.50 would require it to be used?
Around here (DFW, TX area), I rarely see fire sprinkler piping being grounded or being used as a grounding electrode -- it just seems to be ignored -- is there a reason for that?
It looks to me like 250.50 would require it to be used?