Table 514.3(B)(2) says the interior of that dispenser is Class I, Division 1.I'm waiting on classification clarification but there are things here that bother me such as the LFMC.
Any input ?
How about picture 1?The picture (3) is a compressor type device, not a dispenser...
I though it was the interior of the equipment in picture 1....sorry about that.The picture (3) is a compressor type device, not a dispenser...
NFPA 52 only specifies Div. 2 within 15 feet of compression equipment. If this is like other packaged CNG compressors I have seen, there is a cooling fan internal which provides significant ventilation within the compressor enclosure along with a combustible gas detector which will shutdown the unit on a gas leak. Also since I assume this is a pre-packaged skid from the mfr., does Chapter 5 apply?
I would have said that the EGC within the flex conduit would be sufficient but in looking at the section you quoted I don't see anything allowing elimination of the bonding jumper.
In looking at the photos again I am also wondering about the seal fitting location - if you assume the area shown is Division 2, and also assume that the underground conduit run comes back up above grade in a non-classified location, then those seals would be boundary seals and would have to be the last fitting leaving the area (the LBY fittings are between the boundary and the seal in the picture).