danielrourk2015
 - US
Is there a 600 amp rated meter enclosure with 3 separate 200 amp disconnect after the utility side?
Sent from my XT1254 using Tapatalk
TksI have not seen one but there is a 600 amp meter with built in CT's.
I know this pic looks crooked but it is the camerman (not me). This is a meter base with ct's inside for a 600 amp service
Some of the rural power companies around here are using similar CT meters, they are "ringless", instead of a ring securing the meter the cover secures the meter - remove cover and you have access to test switches as well as ability to pull the meter. Cover gets a lock or seal to keep customer out of the meter section.I've never seen one off the shelf....most are custom orders. CT's are sized by the utility as needed. In the picture, it's a new one on me. 600A is a pretty common installation. Lots of different breaker setups. Just make sure you check with your utility/AHJ. I can't really tell where the CT's and associated test switch are installed, but a separate meter enclosure would not fly. If the CT's are inside the meter can, where is the associated test switch? Must not be in the meter can. Can't pull the meter without opening the test switches first, and you can't open the test switches without removing the meter cover, which requires the meter to be pulled first......:? Anybody besides me got a headache yet?
Glad I never ran into one of these!!!!!