Mutiwire Branch Circuits

Status
Not open for further replies.

nhee2

Senior Member
Location
NH
Any reason that a multiwire branch circuit could not feed (2) individual GFI receptacles? Need many outdoor, 20A receptacles for truck parking lot (block heaters). Was planning on 2 gang boxes each with (2) GFI receptacles and trying to limit qty of conductors and conduits required.

Pretty basic but not what I normally do. Assuming its fine code-wise any other reason you would not use MWBC? Accepting that trip of one breaker takes out 2 ckts.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
You don't need to use 2-pole breakers. Handle ties will do.


Even with handle ties when one trips it will open the other circuit.

I guess the good part about handle ties is you can remove the handle and troubleshoot one circuit at a time.
 

jap

Senior Member
Occupation
Electrician
I always used to use the MWBC but that was before tying the handles came into play.
I've never been a fan of tying breakers together for a 120v load just because they share a neutral.
Now I seriously consider pulling the extra neutral if it doesn't crowd the pipe or break the bank.
It's sometime worth it to me not to have to hear all the handle tie vs. 2 pole breaker arguments that keep coming up as evident above.

JAP>
 