A new section was added to 314.16(B)(2) in the 2014. I just saw it yesterday.
I bolded the new wording.
What the heck does it mean? Any example of the box and clamp that it refers to?
(2) Clamp Fill. Where one or more internal cable clamps,
whether factory or field supplied, are present in the box, a
single volume allowance in accordance with Table 314.16(B)
shall be made based on the largest conductor present in the
box. No allowance shall be required for a cable connector with
its clamping mechanism outside the box.
A clamp assembly that incorporates a cable termination
for the cable conductors shall be listed and marked for use
with specific nonmetallic boxes. Conductors that originate
within the clamp assembly shall be included in conductor fill
calculations covered in 314.16(B)(1) as though they entered
from outside the box. The clamp assembly shall not require a
fill allowance, but the volume of the portion of the assembly
that remains within the box after installation shall be excluded
from the box volume as marked in 314.16(A)(2).