Maybe this is the problem.

Status
Not open for further replies.

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
My wife's Aunt wanted to talk to me at the end of their phone conversation. She relayed the story of her main breaker tripping and the neighbor suggesting she call an electrician if it happened again. I suggested we look sooner.
View attachment 14687
Not quite typical, but we've all seen PP connections fail.

View attachment 14688

Maybe this is why the main tripped.
The picture isn't clear, but did they not use the ties for the lugs for that and only terminated to two of the lugs instead of all 4?
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Those are two 2-pole 60 amp 1ph circuit breakers for her electric heat. The connections on one wire of each CB failed badly enough to burn through the side of each CB until the two legs started arcing and sparking enough to trip the 150 amp main.

Simultaneous failure on two breakers, or one burned through to the other?
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Not legal as a field install, but I have seen '4 pole' breakers (2 poles in parallel for each leg) as part of a listed panel assembly.