immensity725
- reading, pa
what would be a good manual motor starter for a single phase,3hp, 230v motor with a fla of 16 amps. I'm using a 35 amp breaker with a 25 amp time delay fusible fuse...the motor is for an exhaust fan...
It does not come with a internal heater..1ph? Have you confirmed that the motor has integral internal overload protection already? If so it's a done deal as far as motor overload protection. Then it's a matter of sizing the wire correctly to carry the load and then protecting the wire with a correctly sized OCPD the way that I see it.
You mean integrated overload protection (a temperature-sensing switch is a common means).It does not come with a internal heater..
An internal heater really is just a heater.
In a starter, and when a part of a bi-metal overload switch (not the electronic OL's).http://www.eaton.com/ecm/idcplg?Idc...veAs=0&Rendition=Primary&dDocName=VOL05_TAB03
pg 11
Eaton calls them heaters
common terminology
Temperature-sensing switches integral with the motor are similar... but they are simply not called heaters, at least not in my neck of the woods... and relatively speaking, that's not all that far from yours.