Just clearing the air.

Status
Not open for further replies.

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
Is knob and tube wire considered copper-clad-aluminum?

And if so, use that column for breaker sizing?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I've never seen any that wasn't copper. Plus all I have see were sizes 14-10 and if protected by today's Code 240.4(D) would limit your breaker size to the 60° rating.
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
I've always wondered but never rose my hand. As sometimes when stripping the insulation off the knob and tube the copper appears to have some cladding to it, maybe it is lead but I don't know for sure.
So what is this copper-clad-aluminum spoke of in the ampacity chart? Don't know if I've ever seen it, maybe some older tw wire that when stripped resembles it?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I've never seen any that wasn't copper. Plus all I have see were sizes 14-10 and if protected by today's Code 240.4(D) would limit your breaker size to the 60° rating.
It is aluminum wire which has a thin layer of copper over it in an attempt to reduce the high resistance connection problems with early aluminum wire.
It does not allow you to use it with Cu-only devices though.
I've always wondered but never rose my hand. As sometimes when stripping the insulation off the knob and tube the copper appears to have some cladding to it, maybe it is lead but I don't know for sure.
So what is this copper-clad-aluminum spoke of in the ampacity chart? Don't know if I've ever seen it, maybe some older tw wire that when stripped resembles it?
 

user 100

Senior Member
Location
texas
Is knob and tube wire considered copper-clad-aluminum?

That old wire is tinned- they did that a long time ago for protection against the corrosive properties of the old rubber insulation, iirc.
Scrape some of tinning and you will see copper. The dead giveaway for tinned vs copper clad is the insulation type of the wire: If rw or rubber like in texture or "feel" it's going to be tinned copper almost certainly- by the time cc al hit the scene rw had been replaced by tw.

To further complicate stuff, I believe that tinned nm with tw insulation was made briefly same as cc al nm . To tell the difference maybe just look at the jacket- if its braided clothy tarry stuff, its most likely tinned copper. If its a slick plastic jacket, probably cc al, as most braided jackets were gone too, afaik, by the time cc al nm came out in late 60's- early-'70s. CC al is also not the silver color of tinned k&t.
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
Anybody got a picture of it?

Thanks I have never heard that before. I've come across aluminum nm but never what you have described.
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
... knob and tube the copper appears to have some cladding to it, maybe it is lead but I don't know for sure. ...

I'm almost certain it's "tinned" copper wire. Soldering was the standard connection method at the time.
("tinned": plated with solder, an alloy of lead & tin, usually 63% Pb / 37% Sn for electrical work)
 

user 100

Senior Member
Location
texas
Anybody got a picture of it?

Thanks I have never heard that before. I've come across aluminum nm but never what you have described.

No pictures that I can find anywhere of the tinned nm but from what I understand it did exist, at least in very, very old nm.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
No pictures that I can find anywhere of the tinned nm but from what I understand it did exist, at least in very, very old nm.

I have some in my scrap collection.

Here is a pic (not so great) from the 'net

Wiring_Fabric_Rubber_PHG_239_DJFss.jpg


From the article:

Tinned Copper Electrical Wire Identification


http://inspectapedia.com/electric/Tinned_Copper_Electrical_Wire.php

Here is tinned KT

kt_conductor.jpg
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
Well, tinned k&t all makes more sense now!
Since the method of connecting and splicing was soldering anyway, and as stated earlier as a barrier from rubber.

Still would like to see some copper-clad-aluminum though, inquiring minds need to know---ya know.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since this thread contains good information regarding different conductor types I've moved here where it's more relevant.
 

Fulthrotl

~Autocorrect is My Worst Enema.~
Well, tinned k&t all makes more sense now!
Since the method of connecting and splicing was soldering anyway, and as stated earlier as a barrier from rubber.

Still would like to see some copper-clad-aluminum though, inquiring minds need to know---ya know.

copper clad aluminum to my knowledge was used briefly during the 1970's in romex, when they had
this spiffy idea that skin effect and the copper plate would make it as good as solid copper for house
wiring.

the practice ended when it was discovered that copper clad set houses on fire as well as straight aluminum.
it was all the rage in 1977 when i started as a muppet. started about 1975, and the show was over by 1980.
 

norcal

Senior Member
I remember seeing "use copper, or copper clad aluminum only" on wiring devices, & always thought CU clad AL's purpose was the "economy" of aluminum, and the ease of termination of copper.
 

Johnnybob

Senior Member
Location
Colville, WA
When I was in grade school, my grama sold a section of land to the Hatler Bros. who turned it into the very first subdivision/housing development in our area. Anyway, the contractors would let me pick up scrap wire for helping clean up around the site. I learned pretty darned quick the difference between copper nm and copper clad nm, the main difference to me at the time being that copper clad didn't buy many ice cream cones:weeping:!
 