ControlThis
- Londonderry, NH
I work in a small industrial facility in which I am working to organize an arc flash safety program. We had a visit from OSHA so we can no longer put this off. I've been looking through NFPA70E for the last 5 or 6 years and just took a course on it recently.
How I should consider the array in terms of available fault current to the building? We have grid tied inverters and no batteries.(150kw total capacity). I know that I need to consider the available fault current from the utility transformer and fault clearing times for our fault protection devices, but what do I do with a feed from the inverters that is parallel to this transformer? Is the AC output from the array to be considered a "transformer" for the purpose of this standard? Would I just add the available fault currents together?
As if NFPA70e isn’t already enough of a pain without an array hooked up, I’m just not sure yet how to deal with these two parallel feeds. Without the array, it seems I can keep the incident energy analysis fairly simple as even the worst case scenario for fault current at the utility's transformer puts us at level 1 PPE.