Water lines running through Electric rooms

Status
Not open for further replies.

drun

Member
Location
San Diego, CA
Anybody know what section deals with water pipes running through electrical service rooms?
We have a 400 amp Motor Control Cabinet with a 5" water pipe running vertically 4" away from the gear. :dunce:
The back-flow valve blew out on this flooding the gear and a painter ran in to turn off the supply valve.
Good thing the GFI tripped before that. Else he'd be dead.
 
Last edited:

dkidd

Senior Member
Location
here
Occupation
PE
Look at 110.26. But unless the pipe is in the required working space, it is not prohibited.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
It isn't unheard of for the sprinkler and domestic water risers to originate in an electrical room.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I know we got turned down once until the fire sprinkler was removed from the electric room.

Must be a local amendment. Nothing in NFPA 13 or 70 prohibits sprinklers in an electrical room.
 
I ran into this problem one time, it was an 8" RO line running vertically next to a 4160 MCC. I would have been ok with it: however, there was a flange about 12" above the MCC.:happysad:
We had a response from one of the design engineers, he stated "it's RO water, it will be ok because it's ~15 Mohm water" :slaphead:. Our suggestion to remove or lower it was shot down because there was no code violation. :rant:
We utilized a flange shroud, so it would direct the water downward.
 