Not open for further replies.

faresos

Senior Member
Hello Everyone,

I have a questions with regards sizing a panel feeding group of motors. There are multiple of motors with different sizes (2)125HP & (3)25HP. The vendor claims the actual HP used for the (2) 125HP is 105 &73HP and for the 25HP's is 20HP. Some of these equipment will have VFD's. My question, can we size our service based on the actual HP used or the motor size name plate (125% of the largest motor and 100% for the rest)?

Thanks,
 

faresos

Senior Member
Thank you all for the replies. I was thinking the same way but I thought I double check if there is some kind of exception that I'm not aware of.