BURGH
- Richmond Va Chesterfield
If you have a 1 amp fuse protecting a device like a transformer. And you want to replace it with a miniature breaker. Do you size the breaker at 1 amp also and if so how do you determine the trip curve?
For something that has a surge of current upon energizing it you may need to look into differences in trip curves of the two different devices just to ensure the startup current doesn't cause nuisance tripping.
The code generally does not require you use a cb rated less than 15 Amps.
The end user is requesting CB instead of fuses
It seems unlikely to me that a xfmr that had its 1A fuse replaced with a 15A CB would ever have trouble with nuisance tripping.
Correct the chance of nuisance tripping is pretty much non existent in that situation, but I was talking about replacing a 1 amp fuse with a 1 amp circuit breaker, or any amp fuse with same amp circuit breaker for that matter.It seems unlikely to me that a xfmr that had its 1A fuse replaced with a 15A CB would ever have trouble with nuisance tripping.
Why would you replace a 1 amp fuse with a 15 amp circuit breaker?
Except you might slag the occasional transformer. Which also might be considered a nuisance.hmy:
Why would it hurt the transformer any? UL product standards have been harmonized with the NEC so since the NEC allows it, the product standard has to accommodate it.
If the transformer requires a 1 amp fuse for protection and you replace it with a 15 amp fuse, what do you suppose will happen when you put a 10 amp load on the transformer?
Guys, it appears that we are talking about a fuse in a piece of utilization equipment that has a transformer, not OCPD for a transformer installed to NEC requirements.
-Jon
I don't see that changes the answer any.
The reality is that if the piece of utilization equipment that has the xfmr in it is listed to UL standards, the same rules would likely apply as if it were a NEC piece of equipment being installed. UL508a would allow for a 15A CB just as the NEC does.
Personally I would not get real excited about the rating of the CB. I am a fan of using the highest rated CB I can most times to reduce the incidence of nuisance trips. I also size fuses that way. Small transformers are infamous for tripping OCPD on the primary side.
Nothing until it is overloaded.![]()