Uh, maybe because if it is a 16A rated cord, it will catch on fire long before a 60A breaker will trip?
rose1981
If the welder has it's own internal 16A circuit breaker, it might be OK technically but at the same time, what I said above still holds true; they likely used some sort of power cord similar to our 12ga, maybe less, whcih is not going to be protected by a 60A breaker. 16A also is a clue that this is a foreign welder, because 16A is an IEC limit for certain harmonics issues (which is problematic for them with portable welders). Because of that, make sure you check that this welder will work here because it was likely designed for 50Hz operation; it shouldn't matter but it might. Also for them, 240V is line and Neutral, which might mean a N-G internal connection which would be a problem here.