Looking for code section requiring air gap for dimmers?

Status
Not open for further replies.

andrew45

Member
Location
La Jolla, CA
You know these things, the little pull tabs at the bottom of electronic dimmers that claim to disconnect the load...

They are sometimes called Front Accessible Service Switch...

I cannot seem to fine the relevant code section.


I did find 404.15 (B) (which is horribly written) which says:

(B) Off Indication. Where in the off position, a switching device with a marked OFF position shall completely disconnect all ungrounded conductors to the load it controls.

However, this does not require an air gap, or even that an electronic dimmer be capable of turning a load completely off by whatever means.

thoughts?
 

andrew45

Member
Location
La Jolla, CA
Lutron seems to think its required...

Lutron seems to think its required...

Lutron seems to think its required, as do lots of others apparently. There's a bunch of patents on how to make them where the text says that.

I happen to think its dumb since there is no guarantee that a remote controlled dimmer is even the correct dimmer to pull the tab on.
 