I will install an outside disconnect (200 amp) beside the meter on a residence. I would like to connect the line conductors from the meter to the two lugs mounted on the two bus bars instead of on the 200 amp breaker itself. (The remodeling situation existing wire length into the house makes this my best option) I have another small breaker I want to install in the disconnect for an outside building. The only thing is, that the house panel will not be fed from it's own breaker. That 200 amp main breaker will feed the bus bars including a 60 amp breaker plus the two lugs on the end of the bus bars that feed the house 200 amp panel. Do you see a problem with this? Thank you