250.54 Auxiliary Grounding Electrodes. One or more grounding electrodes shall be permitted to be connected to
the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode
bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.53(A)(2) Exception, but the
earth shall not be used as an effective ground-fault current path as specified in 250.4(A)(5) and 250.4(B)(4).