Is there a rule that commercial lighting and receptacle circuits can only be 20A?

Status
Not open for further replies.

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
I'm working on the old Snap-On factory in Natick, MA and there are a bunch of NM cables feeding the lights and receptacles for the front office area.

It's a mix of threaded NM and slightly newer NM (but before yellow 12). But one cable is 14 gauge. Of course it was on a 20A breaker.

Even so, is there a rule that says you can't have a 15A receptacle or lighting circuit in a commercial environment?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In some jurisdictions, like NYC where #14 conductors are prohibited for branch circuits, you would see 20 amp circuits for everything.
 

GerryB

Senior Member
I'm working on the old Snap-On factory in Natick, MA and there are a bunch of NM cables feeding the lights and receptacles for the front office area.

It's a mix of threaded NM and slightly newer NM (but before yellow 12). But one cable is 14 gauge. Of course it was on a 20A breaker.

Even so, is there a rule that says you can't have a 15A receptacle or lighting circuit in a commercial environment?
Guess I'll ask. What is threaded NM?
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
Sorry, I meant the old cloth jacket with the undersized ground. "Threaded" made sense in my head when I typed it.

Thanks iwire for the local response.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
"Threaded" is the old type R or RW tinned copper which had fine threads around the rubber insulation.
 
Status
Not open for further replies.
Top