We have converted an old livestock trailer to a mobile mushroom dryer.
One of the things we must have is LOTS of airflow over the mushrooms to ensure they dry out a fast as possible.
We have a large fan to help with this.
Because we will be out in the boonies running this thing we have the following setup:
Generator with single phase 220 volt outlet. This runs through a line reactor to clean up the power then connects to a VFD where it is converted to 480 volt three phase.
Our electrician is talking about running the hot and the common to the line reactor and connecting the ground to the frame of the trailer.
The two outputs from the line reactor (which is grounded to the frame) then run to the VFD.
From the VFD he is taking the Protective Earth and connecting that to the frame.
He is also running the Protective Earth connection from the motor to the frame.
The frame of the trailer will not be hooked up to a grounding spike or plate as we move around far to much for that.
This seems.... Questionable to me.
First of all I am concerned that having the 220 single phase and the 480 triple phase both grounded to the frame will throw the ground fault in the generator all the time.
If that is not a problem what about current leakage and the possibility of someone grounding out when stepping up into the trailer and getting kicked out of the gene pool :?
anyone see a problem with this?
Sean.
We have converted an old livestock trailer to a mobile mushroom dryer.
One of the things we must have is LOTS of airflow over the mushrooms to ensure they dry out a fast as possible.
We have a large fan to help with this.
Because we will be out in the boonies running this thing we have the following setup:
Generator with single phase 220 volt outlet. This runs through a line reactor to clean up the power then connects to a VFD where it is converted to 480 volt three phase.
Our electrician is talking about running the hot and the common to the line reactor and connecting the ground to the frame of the trailer.
The two outputs from the line reactor (which is grounded to the frame) then run to the VFD.
From the VFD he is taking the Protective Earth and connecting that to the frame.
He is also running the Protective Earth connection from the motor to the frame.
The frame of the trailer will not be hooked up to a grounding spike or plate as we move around far to much for that.
This seems.... Questionable to me.
First of all I am concerned that having the 220 single phase and the 480 triple phase both grounded to the frame will throw the ground fault in the generator all the time.
If that is not a problem what about current leakage and the possibility of someone grounding out when stepping up into the trailer and getting kicked out of the gene pool :?
anyone see a problem with this?