Hi everyone
This is my 1st post and i hope that you can help me with this little question that me and my buddies from work have been discusting for the past few days (in advance sorry for my english, im not from USA but we practically use the NEC standards for our wokr)
We need to feed a 150 KVA dry type transformer (480-208Y/277) which is almost 500 feet away from the main panel (we've been looking for a more short distance option but our client is very reluctant about it). This installation will be made in a "supervised location". This transformer will feed a panelboard but the secondary feeder is about 160 feet long, reason why we want to include a main breaker in the 208v panelboard.
Normally we consider 125% of the transformer FLA and use the next size up for the primary OCPD (which is a SQ-D breaker) and based in the size of the OCPD we select the conductor:
FLA (150KVA) = 150000 / (480 * 1.7321) = 181 amp
BKR = 181 x 1.25 = 225 amp
This will give us a 4/0 AWG conductor
Now here comes the discusion that we've had the past few days because for the secondary feeder we usually use the same criteria (125% for the main breaker and select the conductor based on the secondary OCPD).
The article 450.3 indicates that when using a primary AND secondary protection we need to consider a 250% for the primary protection. I have read a lot of articles in this website and also on the internet (EC&M, EEP, even schneider and bussman articles) where they make some examples and even when they say that the OCPD is for the transformer protection and not the conductors they still oversize the primary conductor according to the 250% OCPD.
My biggest question is if my 125% primary and 125% secondary criteria is correct and if not then what would be the right considerations and also the electrical explanation of why consider 250% primary OCPD just when we have a secondary OCPD and not when whe have just the primary OCPD.
I really hope i made myself clear.
Regards
This is my 1st post and i hope that you can help me with this little question that me and my buddies from work have been discusting for the past few days (in advance sorry for my english, im not from USA but we practically use the NEC standards for our wokr)
We need to feed a 150 KVA dry type transformer (480-208Y/277) which is almost 500 feet away from the main panel (we've been looking for a more short distance option but our client is very reluctant about it). This installation will be made in a "supervised location". This transformer will feed a panelboard but the secondary feeder is about 160 feet long, reason why we want to include a main breaker in the 208v panelboard.
Normally we consider 125% of the transformer FLA and use the next size up for the primary OCPD (which is a SQ-D breaker) and based in the size of the OCPD we select the conductor:
FLA (150KVA) = 150000 / (480 * 1.7321) = 181 amp
BKR = 181 x 1.25 = 225 amp
This will give us a 4/0 AWG conductor
Now here comes the discusion that we've had the past few days because for the secondary feeder we usually use the same criteria (125% for the main breaker and select the conductor based on the secondary OCPD).
The article 450.3 indicates that when using a primary AND secondary protection we need to consider a 250% for the primary protection. I have read a lot of articles in this website and also on the internet (EC&M, EEP, even schneider and bussman articles) where they make some examples and even when they say that the OCPD is for the transformer protection and not the conductors they still oversize the primary conductor according to the 250% OCPD.
My biggest question is if my 125% primary and 125% secondary criteria is correct and if not then what would be the right considerations and also the electrical explanation of why consider 250% primary OCPD just when we have a secondary OCPD and not when whe have just the primary OCPD.
I really hope i made myself clear.