Wire and conduit installation

Status
Not open for further replies.

rey-man

Senior Member
Location
New york
When estimating for the installation of conduits and wire, does the following inclusive of the take-off?

For wires,

- cable dressing
- grounding
- termination

For conduits,

- termination

Thanks for your help.

Sent from my SM-N920T using Tapatalk
 
My junction box assemblies include labor for terminating and bonding.

On conduits, I'm guessing you are talking about couplings and connectors? You should have labor added for each of those as well.

Device assemblies include labor for a connector and bonding jumper, as well as box brackets, screws, etc.....


Sent from my iPhone using Tapatalk
 
Its pretty much about terminating conduits to enclosures and landing wires at terminals.
Preparing the wires for termination should be part of its installation, right?
Thanks again.

Sent from my SM-N920T using Tapatalk
 
Wire and conduit installation

Sure ..... I include that labor in my junction box assemblies, not conduit and wire pulls

Larger boxes will have more connectors and terminations to make, so more labor

Sent from my iPhone using Tapatalk
 
Wire and conduit installation

I personally do not ..... I have that included in my junction box/device/fixture assemblies.

Edit..... I mean it is a line within my assembly, but it doesn't show us separate in a bid breakdown

Sent from my iPhone using Tapatalk
 
Status
Not open for further replies.