llewis
Member
- Location
- Oxford, GA, USA,
I have a motor that is only protected by a Breaker with a switch, however the breaker is tripping, I believe the breaker is not able to handle the inrush current, it was originally sized at about 125% above the FLA. It is a QOB which is an inverse time type breaker and according to NEC Table 430.52 I am able to go 250% above. I had seen a similar comment recently and one moderator suggested even thogh the NEC would allow 250%, he suggested only 150%. Am I correct in looking at the code this way? is there any suggestions otherwise?