andykee
- United States
If I have a 3 phase combiner panel with 240v on a single phase(435v ph-ph), can I feed each hot pin of a nema6 15 outlet from the same phase to get 240v?
That was what I thought, so is a small step-down transformer the best solution?
Two conductors from the same phase gives you 0 volts.
How many conductors are there on a single phase?
He said he got 435 volts on a single phase. I took it that he was asking if putting a 240 volt receptacle on that phase was acceptable.
It looks like you took it as each conductor was a 'phase' and two parallel conductors were going to be run to the receptacle from a single conductor, which would indeed give 0 volts from conductor to conductor.
I think we may need some clarification from the OP.
I think it is clear
I was working through an enphase design guide and saw they had a nema 6 15r plug on a monitoring device (250v envoy-c) wired in to a 480v panel and was wondering how to wire it. (screenshot attached)
Not so much as you think. What is the definition of a phase? To me, a phase IS two conductors. To others, it is a single conductor.
It depends on whether the receptacle is rated for 240 to ground or only 120 to ground. Same issue as slash rated breakers.So if the system is 422Y/244 V can I wire that outlet as L1 and Neutral on each of the receptacle horizontal pins?
The only issue I see with that is a NEMA 6 outlet is marked for two ungrounded conductors and you will have an ungrounded and a grounded conductor.
It will work but I am not sure if it is a listing violation.
That was my concern, too. Using, instead, Nema 7-15 for 277 volts would only have one hot, as it would be one leg of a 480 volt three phase to neutral, meaning only one ungrounded connector.
But then, it's a 277 volt design fed with 240-250 volts.