jpelectrical
Member
- Location
- Saint Cloud, Fl USA
This is a discussion my Master and I are having with what appears to be a contradiction to 314.16 (c) with 250.148. He is saying that you can not splice or terminate equipment in a conduit body unless it can be grounded to the body. I say as long as i am not connecting any equipment in the conduit body this does not apply to splicing conductors in the conduit body that is clearly marked and labeled with the cu in.
Also the code says that if
Splices are made in a conduit body then it is then considered a "box".
This is an industrial application with rigid conduit that is bonded the the steel structure.
Trying to upload the statement in the code book were i took a picture and try and get it on here NEC 2011
Also the code says that if
Splices are made in a conduit body then it is then considered a "box".
This is an industrial application with rigid conduit that is bonded the the steel structure.
Trying to upload the statement in the code book were i took a picture and try and get it on here NEC 2011