mikewright
Member
- Location
- Danville, Illinois
This exists in a healthcare facility. There are many issues with this panel. Please let me know what the issues are to support my concerns. Thanks!
Sent from my iPhone using Tapatalk
You do not have a panel. You have a field created 'junction box'
Other than what looks like a bunch of ground wires crammed into a single lug, there is not enough information for me to pass judgment on it.
Are the brown wires connected to the neutral bar?
None of those are code violations however seeing the neutrals terminated on the same buss bar is a problemAlso, butt splices and shared 120/208 277/480 neutrals and raceways.
Has anybody actually done any monitoring to see what the THD is?With the shared neutrals of the 120/208 transformer- my harmonics are not harnessed creating THD.
None of those are code violations however seeing the neutrals terminated on the same buss bar is a problem
Has anybody actually done any monitoring to see what the THD is?
What type of equipment is being served with the 120/208?
Roger