Equipment GroundingConductor

Status
Not open for further replies.

smallfish

Senior Member
Location
Detroit
Does the National Electrical Code 2014 allow the electrical metallic tubing enclosing feeder conductors run from Service disconnect to distribution panel to serve as a means of equipment grounding or must a wire-type equipment grounding conductor be run with the feeder conductors?
Thanks
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Does the National Electrical Code 2014 allow the electrical metallic tubing enclosing feeder conductors run from Service disconnect to distribution panel to serve as a means of equipment grounding
Yes. Be sure and check out 250.94.
or must a wire-type equipment grounding conductor be run with the feeder conductors?
Thanks
No, not required.
 