Outlet box placement
Not illegal, tho there appear to be 2 code violations there: no staple within 12" of the box on the bottom piece of NM, and drywall cut more than 3/16" around box (hard to tell).
Those type of boxes require the staple to be within 8". Nothing wrong with the proximity to the shower body.
Pretty sure the rule is 1/8" not 3/16", but a little drywall compound or about anything non combustible will make it compliant.
Youre right; 312.4. Maybe was thinking 3mm = 3/16", which it doesnt. Also was thinking the OPs box with those wings qualified as clamps, thus the 12" mention vs 8" for boxes w/o clamps.
Thank you for the replies. My co-worker was arguing with me about whether or not that box was in a wet location.
Tell your co-worker there are building codes for wet locations and standard studs and drywall do not meet those rules.
What wings - that is a nail on box and it has no integral clamps.
Look at the top left or the box with the 2 NM thru it- the piece of plastic between the two - when I first saw the pic I was thinking that was a clamp, but it isnt, just a pre-punched KO.
I saw that right away. Seems to be typical for that box to just spin the KO 90 degrees and then insert cable, I never gave it any thought as to being a clamp as I have seen them that way many times.
If the box doesn't have a clamp you have no choice and must staple within 8".
One gang box however is the only box allowed to not have a clamp.