Load Calculation sample
Transformer rating
Transformer rating
Thanks. I have a doubt in calculating the size of transformer. I got my main panel rating as 180 kVA now how to choose the rating of Transformer?
The transformer’s MVA rating is usually determined based on the system expected load growth, available generation and expected rate of return on the investment. The business plan is based on capital cost recovery, depreciation rate and the profit to be made each year. Transformer applications such as two winding, autotransformer, step-up or step-down etc. influence the transformer rating. Other factors such as expected power demand growth and load factor have a large influence in determining the transformer rating.
The supplied equipment as induction motor starting current and maximum voltage drop permitted could also influence the transformer rating [As a rule of thumb the transformer power should be 3 times the biggest induction motor starting D.O.L.]
Expected Growth
Expected Growth
Please do not take this as a challenge. Is there a code reference mandating perspective growth as part of a calculation? I agree this may be a best practice, but I would love to show a potential client the mandate that makes sizing items larger than is immediately necessary. I hate perfectly sized the firs time, but some clients hate the additional cost to go bigger (rather short-sighted, but a reality)
thanks!
thanks!
Even if you come up with an actual summary of all your connected load and have a kVA value, you can't buy that exact transformer size! That said, you will secure a transformer that is sized a bit larger than what your requirement says. The next higher size might be 25% larger than your requirement, maybe 30% larger, etc. Show your client the options and make them happy. Why not?
thanks!
No there is no such thing as factoring in for or guessing what may be added in the future.
Calculations are strictly based on the information provided on THAT install only.
It's not common sense...
It's Code.
Sent from my SAMSUNG-SM-N910A using Tapatalk