Hello All,
I have a panel with a 7 1/2hp motor and electric drive. Along with other peripherals like a power supply and relays. The total calculated FLA for the panel is 42amps. In the past, this panel is being built with a 60A disconnect. Recently, it has been brought up that the Electric Drive is fused at 90A, according to manufacturer, therefore the disconnect has to be atleast 115A.
I changed it, now the customer is saying he has to put in larger service since the panel is above 60A. Is the customer correct? If he only needs 42amps to run the panel, why should he put more than the 60a service he has currently? Is there code on this? Why would less service be bad?
Thanks, Larry
I have a panel with a 7 1/2hp motor and electric drive. Along with other peripherals like a power supply and relays. The total calculated FLA for the panel is 42amps. In the past, this panel is being built with a 60A disconnect. Recently, it has been brought up that the Electric Drive is fused at 90A, according to manufacturer, therefore the disconnect has to be atleast 115A.