You can equally well say that the arc resistance decreases as the current increases.The arc resistance does not obey ohm law: it decreases with increase in voltage across it.
But that does not make my point clear :You can equally well say that the arc resistance decreases as the current increases.
Arc flash hazard increases with voltage. 480V is more dangerous than 240V in that respect.
I missed seeing the post#18.Unless you respond to post 18 anything you have to say is just a distraction.
True. But here the discussion is more about the inherent nature of safety 480V Vs 240V than due to effect of delayed operation of associated OCPD's making 240V more dangerous arc flash hazard than 480V.The fact is that 240 can and often does present a greater arc fault energy than 480.
What is the bolted fault current values you took for 480V and 240V? They can not be same. The bolted fault current value for 480V is greater than 240V (Ohm law) and so the arcing current, arc hazard and incident energy level all should be higher for 480V per formulas of the same IEEE 1584 inConsider 2 systems:
1. 45kVA dry type transformer, 480Y/277 V secondary, 5% Z (primary volt irrevelant), connected to an infinite bus, with secondary connected to a panel. Ignore any conductors.
2. 45kVA dry type transformer, 240V delta secondary, 5%Z, connected to an infinite bus, with secondary connected to a panel. Ignore any conductors.
So the 2 systems are similar. Choosing some values for the incident energy equations:
Trip time 2 sec
Gap is 25mm
Working distance 455mm (18 in)
Enclosed box
Using the IEEE 1584 equations, the following incident energy levels are found:
480V is 5.3 cal/cm^2
240V is 11.2 cal/cm^2
So, is the higher voltage resulting in a higher incident energy value? I have provided all the values for you to duplicate using the IEEE 1584 equations.
http://arcadvisor.com/faq/ieee-1584-calculation-procedure
As a worker that gets exposed to an arc flash and receives burns because of it, you don't get burned by the amount of current that flows, you get burned by the radiant heat that is given off from the incident, or even molten metals that get thrown at you. Regardless of voltage it is the number of calories you are exposed to that determines how badly you will get burned. Lower voltage could expose you to less instantaneous calories but the incident may last for longer time which still raises the total calories of the event.
There's the heart of the matter right there. Well said.As a worker that gets exposed to an arc flash and receives burns because of it, you don't get burned by the amount of current that flows, you get burned by the radiant heat that is given off from the incident, or even molten metals that get thrown at you. Regardless of voltage it is the number of calories you are exposed to that determines how badly you will get burned. Lower voltage could expose you to less instantaneous calories but the incident may last for longer time which still raises the total calories of the event.
Great put down, (The Three) Musketeers!![]()
Really?!Sahib, there is no put down there.
I did not ignore their clarification and I acknowledged it with thanks; only you do not get it as usual.There is frustration that people take the time to explain to you and show you where you are mistaken and you ignore it.
Thanks, guys, for clarifying that 480V is more dangerous than 240V if not limited by transformer capacity.