Early Parallel feed
Why not tell us what you think and then we can offer some opinions.
Roger
Around here, the utility has strict requirements on conduit sizes for different size services. I'd start by contacting your utility.
Sent from my SAMSUNG-SM-G930A using Tapatalk
Best what to feed 600 amp service
I am install a 600 amp 3 phase service. I believe I need two 3-1/2" PVC schedule 40 conduits with 300 mcm paralel feeders from the transformor to the 600 amp distrubution panel with # 1 ground. The reason for the question is, they are requiring two 4" conduits for future to PP-3 and PP-4. When I need 3-1/2 why wound they want 4"?
Who is doing this design, the Power Company or a design engineer? If they are giving you the conduit sizes aren't they also giving you wire sizes?
If this is a service you won't need the EGC
In many designs conduits are oversized and if you included it in your proposal you should just put them in and get paid.
Roger
You may comply with NEC with 3.5" but that doesn't mean a POCO or even local codes can't still require 4". Ask them for the reference to their requirement if it is beyond NEC. If they have a standard that applies to everyone then follow it. If they are shooting from the hip - good luck with other dealings with them.
Integer inch sizes of conduit are a lot more common, and a lot easier to get. Occasionally you may find fitting product families that mysteriously omit certain half inch sizes.
Here's an example of an expansion coupling that omits the 3 1/2" size, for reasons I don't understand.
https://www.rexelusa.com/medias/sys...&realname=Bizline-RH_Bizline-RXP_24_CT_FS.PDF
Over 2 inch maybe, 1/2, 3/4, 1-1/4, 1-1/2 are pretty common both pipe and fittings in about all types of conduit.
Even 2-1/2 is pretty common.