Apprentice_617
- California
It could be used for either, but given there is already a neutral bar, it was likely intended for an isolated ground.
It can also be used as the equipment grounding bar as long as a path to the feeder EGC is provided.
It could be said to when it is terminated to the combined neutral and EGC bar at (or near) the service disconnect. Not before that point.Does the IG ever bond with the EGC?
Yes, it is required to do so...the connection is at the main or system bonding jumper, which ever applies to the installation.Does the IG ever bond with the EGC?
While I agree that they can all terminate at the grounding bar in the panel, it is expected that the isolated ground conductor terminate at the main or system bonding jumper. The isolated conductor is permitted to pass through panels and enclosures without a connection to get back to the main or system bonding jumper. It would connect at the main bonding jumper for a service supplied system, and at the system bonding jumper for a system supplied from a SDS.Yes, all your egc's and iso grounds can terminate at the same grounding bar in the panel.